Lateral movement (1 Viewer)

outward bound

Well-known member
Joined
Apr 23, 2010
Messages
304
Reaction score
0
When.people or people and materials are being moved on a walking platform lateral movement will be created. How do you work out how much force is exerted in the lateral direction.
 
This is usually calculated as a percentage of the vertical live load and varies depending on the work being carried out between 2.5% and 30%. i.e. if you have 10 kN live load acting vertically on the platform, you might use 10% acting horizontally which would give you 1.0 kN horizontally. Please bear in mind that BS EN 12811 specifies a minimum load of 0.3 kN per bay. There is also a minimum requirement of 2.5% for nodal stability (bracing) of the standards, which also takes account of out-of-plumb (erection tolerances) and should be applied to the total load, not just the live load. BS 5975 covers these requirements better than TG20 or EN 12811. Wind loads would not normally be applied at the same time as lateral loads from live as it is unlikely that people will be working on the scaffold in the maximum wind conditions.
 
Thanks biffo, totally makes.sense but I guess it could be used if it was sheeted.
 
Given that we deign scaffolds for 90mph + wind loads, there would be nobody on site at these wind speeds therefore no live load.
 