Cantilever formula (2 Viewers)

pride2iceman

Member
Joined
Aug 12, 2010
Messages
22
Reaction score
0
Hello, gents!

i am new here, and i am looking for a formula to solve a calculation for a cantilever.
Please see attached!
A solution would be much appreciated!
Would be possible to solve this in Robot from Autodesk?
 

Attachments

  • cantilever_Page_1.jpg
    cantilever_Page_1.jpg
    6.4 KB · Views: 164
Last edited:
Safety factor. Some people use a factor of 4.
 
Hello, gents!

i am new here, and i am looking for a formula to solve a calculation for a cantilever.
Please see attached!
A solution would be much appreciated!
Would be possible to solve this in Robot from Autodesk?

Some considerable time ago I created a simple spread sheet for cantilevers PM me a mail ID if you think it would be of use
Alan
 
Just to interfere here. Be careful with the 3 times and 4 times safety factors chaps.
Work out what the force f is under the applied loading including the self weight of the beam and then decide how you are resisting it. If you were using kentledge, every 1 kg that you add to the kentledge increases the load on the edge of the slab by 1 kg. If you need 1500 kg as in this case to balance the cantilever and that is what you put on it, the load on the edge of the slab is 25 kN (plus self weight). If you multiply the 1500 kg by 4 and put 6000 kg, the load on the slab edge increases to 70 kN which it might not be able to carry.
If you punch off the slab above you are limited by the weight of the slab above to how much force you can apply but assuming there is sufficient weight the load on the slab edge from the beam will only be enough to balance things ie 25 kN.
If you anchor down to the bottom slab, the same thing applies. Here, though, you have a fixing that you may want to over specify to give you confidence that it won't pull out. 15 kN might require 2 no 7.5 kN fixings but you could put a greater number in to give a better safety factor than normal to allow for bad workmanship. On suspended loads a factor of safety of 3 is considered normal (see EN13155) so may be right here but this is the factor between the failure load and, in this case, the working load of 15 kN. A fixing rated at 7.5 kN safe working load already has a factor of safety on its failure load and may not fail until a load of 23 kN is applied to it giving you a factor of safety of 3.
Using serviceability analysis, I would work out the actual load without factoring and then use engineering judgement to decide the type & capacity of the means of resisting it, taking account of the whole situation.
Using ultimate analysis, I would vary load and material factors to suit the situation.
If I was working on site and I saw some anchors that I hadn't put in stopping me toppling off the building with the cantilever, I would probably put a couple of props off the structure above to be sure, to be sure!
 
Just to interfere here. Be careful with the 3 times and 4 times safety factors chaps.
Work out what the force f is under the applied loading including the self weight of the beam and then decide how you are resisting it. If you were using kentledge, every 1 kg that you add to the kentledge increases the load on the edge of the slab by 1 kg. If you need 1500 kg as in this case to balance the cantilever and that is what you put on it, the load on the edge of the slab is 25 kN (plus self weight). If you multiply the 1500 kg by 4 and put 6000 kg, the load on the slab edge increases to 70 kN which it might not be able to carry.
If you punch off the slab above you are limited by the weight of the slab above to how much force you can apply but assuming there is sufficient weight the load on the slab edge from the beam will only be enough to balance things ie 25 kN.
If you anchor down to the bottom slab, the same thing applies. Here, though, you have a fixing that you may want to over specify to give you confidence that it won't pull out. 15 kN might require 2 no 7.5 kN fixings but you could put a greater number in to give a better safety factor than normal to allow for bad workmanship. On suspended loads a factor of safety of 3 is considered normal (see EN13155) so may be right here but this is the factor between the failure load and, in this case, the working load of 15 kN. A fixing rated at 7.5 kN safe working load already has a factor of safety on its failure load and may not fail until a load of 23 kN is applied to it giving you a factor of safety of 3.
Using serviceability analysis, I would work out the actual load without factoring and then use engineering judgement to decide the type & capacity of the means of resisting it, taking account of the whole situation.
Using ultimate analysis, I would vary load and material factors to suit the situation.
If I was working on site and I saw some anchors that I hadn't put in stopping me toppling off the building with the cantilever, I would probably put a couple of props off the structure above to be sure, to be sure![/QUOTE


I was talking about pure kentledge as opposed to using anchors. I assume the safety factor of 3 is still relevant there?
 
if someone have the cantilever formula to calculate the cantilever scaffold platform of
thank you for your help :)
 
Top Bottom