    Hi all,

    Wonder if anyone can help? I'm trying to find the maximum shear capacity of a typical 305mm deep steel ladder beam.

    I can't seem to find this anywhere on the web and suppliers only appear to be able to produce basic loading data sheets, without the shear capacity!

    This may be given in BS EN 39, but I don't have access to a copy unfortunately.

    If anyone could please provide a value backed up by the source of the info, it would be much appreciated,


    Thanks in advance,

    1006

  2. #2
    Join Date
    May 2010
    Location
    This Septic Isle
    Posts
    1,462
    Thanks
    1,390
    Thanked 628 Times in 397 Posts

    Default

    I'm sure its :
    Allowed Shear 12.5kN
    In Britain we used to drive on the left of the road.

    Now we drive on what's left of the road

  3. #3
    Join Date
    Jun 2010
    Location
    North East England
    Posts
    171
    Thanks
    10
    Thanked 64 Times in 53 Posts

    Default

    14.9kN shear from the details I have. I don't think any of the data sheets (Boulton and SGB) I've seen state this, just Safe Working Loads. Our Engineer has worked it back over through calculation to get the maximum shear and bending loads.

  4. #4
    Join Date
    Oct 2011
    Posts
    6
    Thanks
    0
    Thanked 2 Times in 1 Post

    Default

    cheers for info gents,

    i have heard from a few sources that the shear capacity is around this area (12-14kN). To be honest i'm massively surprised how low that is when compared to standard scaffold tube with safe working shear of 29.2kN (according to TG20:08).

    I would expect the weld to be the weak point; but still, bearing in mind the rungs act under compression and you have 2No tube-chords resisting the shear, just seems low.

    Anyhow, could still do with an actual figure & source to back it up if anyone has this, thanks again

  5. #5
    Join Date
    Mar 2010
    Location
    Edinburgh
    Posts
    122
    Thanks
    8
    Thanked 81 Times in 47 Posts

    Default

    We have tested the steel ladder beams and the ultimate shear limit is 40.0 kN which we reduce by a factor of safety of 2 to give a safe working shear of 20.0 kN.
    SGB sure beams (ladder beams) have a maximum shear of 18.0 kN on their data sheets.

  6. #6
    Join Date
    Jul 2010
    Location
    United Kingdom
    Posts
    1,101
    Thanks
    411
    Thanked 1,023 Times in 547 Posts

    Default

    The OLD SGB figure for shear in a Sure Beam was always taken at 18kN. That said I have theSGB data sheets which I must admit are old 1998 and I do not believe they show a shear load. They do however give max allowable point loads and UDL's for various spans. Working backwards from the 1.52m span with 35.66 kN allowable UDL would appear to indicate an allowable shear of 17.8kN.

    It is worthy of note that there are many varying "ladder Beam" designs.
    When I started there were two similar beams one was a Sure Beam and the other a Ladder Beam one was 14" overall depth the other 14" centre to centre.
    I have allways considered the correct construction for the beam to be a saddle cut and a full circumference weld.
    Today you will find beams with flat ends on the verticals which is a much smaller weld surface in a much more confined area. There are also copy beams on the market with sub standard tube not the original 4mm to 1139 or the 3.2mm grade 50C.

    If you are buying beams you need to obtain adequate information from your supplier if you are using existing stock you should take the time to look at what you have and make suitable allowances.
    I hope this is of help
    regards
    Alan
    Last edited by Alan Reade; 13th December 2011 at 10:59 AM.

  7. The Following User Says Thank You to Alan Reade For This Useful Post:

    SWIFTY (12th October 2012)

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

New To Site? Need Help?